Electrical Substation and NFPA 497

Status
Not open for further replies.

ksavoie

Electrical
Mar 6, 2006
24
Is there any rule in the NFPA that will not allow for an Electrical substation with positive pressure ventilation in a Class 1 Div 2 area, within 40 feet from a gas heater?
 
Replies continue below

Recommended for you

There are basically three NFPA documents (70, 496, and 497) that collectively address your question.

Assuming NFPA 497 was the Standard used to determine the electrical area classification and NFPA 496 was the Standard used to design/maintain the pressurization of the substation, NFPA 70 (the National Electrical Code) would permit the installation you have described.
 