Elevator Disconnect Location

Status
Not open for further replies.

mvsubstation

Electrical
Aug 5, 2003
34
I have an elevator machine room elevated above the penthouse floor. The machine room contains the elevator controller, therefore I have shown the disconnect located next to the elevator controller to meet the National Electric Code requirement for the disconnect to be within site of the elevator controller. There is no door into the elevated platform, only a set of stairs that goes down to the penthouse floor. However, it appears the elevator code ASME/ANSI 17.1 requries the disconnect to be on the strike side of the entrance door to the machine room. The elevator contractor says an additional disconnect is required next to the entrance door of the penthouse to meet the ASME/ANSI requirement. Is this true? Could having two disconnects in series be a violation of the NEC which requires one disconnect to remove power from all ungrounded conductors for elevators?
 
Replies continue below

Recommended for you

The elevator machine room should be a room dedicated to the elevator equipment. I have had experience in which walls were constructed about the equipment and all forgien equipment/piping/wiring had to be removed from the elevator machine room. You are required to provide a disconnect upon entering the door to the machine room.
 