buzzp
Electrical
- Nov 21, 2001
- 2,032
I have taken over a project in the US where a 200HP, 460VAC motor burned up. The only protection, which was in place, was the 'Over Temp Protection 2', per the MG standard. This is essentially a thermostat wired into a NC contact. After reading an older version of the MG standard, this thermostat has a fixed trip point of 190C (correct me if I am wrong).
The motor in question is rated for 40C ambient with an insulation class of F (max temp of 155C).
It would seem to me if the motor did reach this temperature and was taken off line, the motor would still continue to heat up beyond the trip temperature of 190C, probably well passed the 195C rating of the insulation. This is also a TEFC motor. I am looking to those with more experience with this type of protection to provide some feedback based on personal experience.
The motor in question is rated for 40C ambient with an insulation class of F (max temp of 155C).
It would seem to me if the motor did reach this temperature and was taken off line, the motor would still continue to heat up beyond the trip temperature of 190C, probably well passed the 195C rating of the insulation. This is also a TEFC motor. I am looking to those with more experience with this type of protection to provide some feedback based on personal experience.