bacon4life
Electrical
- Feb 4, 2004
- 1,518
I am going to be purchasing a new 230/115 kV auto transformer and am considering what kind of tertiary, if any to specify.
The bank this is replacing originally had a 13.8 kV tertiary connected synchronous condenser, however that was removed a decade ago. There are no plans to use the tertiary for power factor correction or customer load, although it might be a backup source for station service. Any thoughts if a tertiary is even required, and if so, whether it should be brought out for possible use as station service or just embedded to protect against faults?
One of the possible reasons for a tertiary is for 3rd harmonics or voltage unbalance. All of our 115/15 kV transformers are delta-wye, so I don't think there should be much 3rd harmonic. However I have been unable to check what the actual harmonic levels are.
For reference, thread238-125717 was somewhat similar.
The bank this is replacing originally had a 13.8 kV tertiary connected synchronous condenser, however that was removed a decade ago. There are no plans to use the tertiary for power factor correction or customer load, although it might be a backup source for station service. Any thoughts if a tertiary is even required, and if so, whether it should be brought out for possible use as station service or just embedded to protect against faults?