fastline12
Aerospace
- Jan 27, 2011
- 306
We are working out some calculations for depth and diameter for posts in a post frame building. We are coming up with some rather ridiculous values. Not off the wall, but certainly way conservative.
So we decided to examine something that works.....electric poles. By our calculations and soil mechanic values based off the EP486. from the ASAE and IBC, we are looking at electric poles needing embedment depths of 14ft or more. We already know they are being installed at 4-6ft and usually just break off well above the ground line here.
So we have a feeling either our math is right and our soil data is wrong, or we have our zeros mixed around....
Based right out of the EP486.1, we have some design values for our soils somewhere around 400lb/ft2*ft. We also have concrete backfill in ours which further increases the area.
I am curious how we might verify or obtain more accurate soil data in our area to verify this part of our work?
Right now we have columns spaced on 12ft centers, 5ft deep, with 3ft diam of concrete around the side wall columns.
So we decided to examine something that works.....electric poles. By our calculations and soil mechanic values based off the EP486. from the ASAE and IBC, we are looking at electric poles needing embedment depths of 14ft or more. We already know they are being installed at 4-6ft and usually just break off well above the ground line here.
So we have a feeling either our math is right and our soil data is wrong, or we have our zeros mixed around....
Based right out of the EP486.1, we have some design values for our soils somewhere around 400lb/ft2*ft. We also have concrete backfill in ours which further increases the area.
I am curious how we might verify or obtain more accurate soil data in our area to verify this part of our work?
Right now we have columns spaced on 12ft centers, 5ft deep, with 3ft diam of concrete around the side wall columns.