Mikey44
Electrical
- Jul 15, 2011
- 3
I plan to install a 750KVA 2400V-480 Delta-Wye XFMR with a high resistance ground. There will also be a 200KW emergency generator that feeds the emergency panel through an ATS on loss of the 750KVA XFMR power. I have limited space to add an additional HRG and would like to use a single HRG, connect the neutrals from both the generator and the XFMR together, then run through the HRG. I realize there is a safety concern when performing maintenance on either the generator or the transformer that up to 277V to ground could be seen on the neutral if there is a ground fault on the operating power source. I plan to deal with the safety issue with warning labels on the equipment and notes on the drawings and may also add a disconnect to each neutral to isolate during maintenance. Are there any issues/concerns/recommendations with this approach? Thanks in advance