I am on site and they have a Em Gen module supplied by Aggreko. It is a Cummins genset 835kW. They went for a start a few days ago and it wouldn't start.
I am on site to maintain their UPS systems and they asked if I would have a look.
The batteries were at 24Vdc (should have been between 27.2V to 27.6V wet lead acid). There are two batteries strings which are selected manually for duty start. The battery is nominal 24V with 2 x 12V 900CCA batteries.
There are two 24V 35A chargers each supplying their dedicated battery. Both of the charger healthy lights were on. The problem was found to be the charger output fuse being ruptured on both chargers. This output fuse is rated at 100A.
The fuses were replaced and the chargers started to supply the battery with current that was limited by the charger at approximately 28A by the charger current limit. The batteries were left for a day to charge up.
The following day both battery strings were checked and found to be at 27.3Vdc.
I connected a scope on the output fuse, monitoring voltage and current. The genset was then started. Voltage at charger dipped to 14Vdc, current was measured at 74A for 3 seconds. The genset started without any problems.
The scope was then attached to the battery and the same test was performed. Battery voltage dipped to 17V and current was measured at 1500A! On no occassion did the fuse blow.
It was then discovered speaking to other on site personnel that the fuses blowing was a reoccuring issue.
Therefore I have two questions:
1. Should a genset this size be taking 1500A to start?
2. Has anyone had any experience with genset chargers overshooting the current limit on genset start up and blowing charger output fuses?
Thanks for any help.
UPS engineer
I am on site to maintain their UPS systems and they asked if I would have a look.
The batteries were at 24Vdc (should have been between 27.2V to 27.6V wet lead acid). There are two batteries strings which are selected manually for duty start. The battery is nominal 24V with 2 x 12V 900CCA batteries.
There are two 24V 35A chargers each supplying their dedicated battery. Both of the charger healthy lights were on. The problem was found to be the charger output fuse being ruptured on both chargers. This output fuse is rated at 100A.
The fuses were replaced and the chargers started to supply the battery with current that was limited by the charger at approximately 28A by the charger current limit. The batteries were left for a day to charge up.
The following day both battery strings were checked and found to be at 27.3Vdc.
I connected a scope on the output fuse, monitoring voltage and current. The genset was then started. Voltage at charger dipped to 14Vdc, current was measured at 74A for 3 seconds. The genset started without any problems.
The scope was then attached to the battery and the same test was performed. Battery voltage dipped to 17V and current was measured at 1500A! On no occassion did the fuse blow.
It was then discovered speaking to other on site personnel that the fuses blowing was a reoccuring issue.
Therefore I have two questions:
1. Should a genset this size be taking 1500A to start?
2. Has anyone had any experience with genset chargers overshooting the current limit on genset start up and blowing charger output fuses?
Thanks for any help.