Reesh14
Electrical
- Aug 3, 2005
- 38
I am installing a new 50kw emergency generator for an existing office building. I am having trouble sizing the necessary wires for design. Inside the building there is an 80A emergency panel that will be wired to a 200A, 3phase, automatic transfer switch. The building uses 120/208V. The automatic transfer switch is wired to a 1200A Main Distribution panel as well. In design, I believe that the load breaker for the generator must match the size of the emergency panel, so it would be 80A/3p. I size the wire from the generator to the ATS for 80A. Do I size the wire from the ATS to the emergency panel for 80A as well? Now for the wire from the MDP to the ATS, I am not sure whether to size it for 200A or 80A? Right now I designed to have a 200A breaker in the MDP for the ATS and sized the wire for 200A. I was told that I do not need to size it for such a high amperage, so I am not sure what to do. I am sorry if this is really confusing to read, but I would appreciate any advice or recommendation of where to learn this design concept. Thank you.