My understanding of an emergency panel is that it has to be connected ahead of main service switch so in case of a loss in power due to a short circuit , the emergency lights will stay on.
I am looking at some design drawings and i see that they connected emergency lights through a circuit breaker in a regular panel and marked it as "locked in an ON position" , my question is what is the point of this? if you have a short circuit on the panel, the main breaker feeding the panel will trip and doesn't matter if my emergency lights circuit breaker is ON or Off anymore , because there will be no power to the panel! also according to NFPA 101 chapter 7:
7.9.2.2* The emergency lighting system shall be arranged to provide the required illumination automatically in the event of any interruption of normal lighting due to any of the following:
(1) Failure of a public utility or other outside electrical power supply.
(2) Opening of a circuit breaker or fuse.
(3) Manual act(s), including accidental opening of a switch controlling normal lighting facilities.
and i think this disqualify the existing design of emergency lighting system!
I am looking at some design drawings and i see that they connected emergency lights through a circuit breaker in a regular panel and marked it as "locked in an ON position" , my question is what is the point of this? if you have a short circuit on the panel, the main breaker feeding the panel will trip and doesn't matter if my emergency lights circuit breaker is ON or Off anymore , because there will be no power to the panel! also according to NFPA 101 chapter 7:
7.9.2.2* The emergency lighting system shall be arranged to provide the required illumination automatically in the event of any interruption of normal lighting due to any of the following:
(1) Failure of a public utility or other outside electrical power supply.
(2) Opening of a circuit breaker or fuse.
(3) Manual act(s), including accidental opening of a switch controlling normal lighting facilities.
and i think this disqualify the existing design of emergency lighting system!