Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Emergency Vent with Manhole with long Bolts

Status
Not open for further replies.

Clamont

Mechanical
Dec 10, 2012
40
I was recently given the calculation for emergency venting as per NFPA 30 using a "manhole with long bolts" 22.7.3.2.1 (2) as per the below.

CFH = 1,667*Cf*A*√(Pt-Pa)

Where;
Cf = Flow coefficient of valve (set at 0.5)
A = Area of open manhole or area of manhole lift
Pt = Absolute pressure inside the tank (inH2O)
Pa = Absolute pressure outside of the tank (inH2O)

My questions is as per below;

1) Is this calculation correct and where can I verify it?

2) How do you determine the pressure when the manhole cover is in the fully open position as required by NFPA 30 22.7.3.10 (2). I can easily calculate the opening pressure however do not know how to calculate the pressure when fully open assuming I had a predetermined length of bolt.

I look forward to replies.


 
Status
Not open for further replies.

Part and Inventory Search

Sponsor