EMF between phase buss

Status
Not open for further replies.

bgdiablo

Electrical
Mar 27, 2007
2
Looking for way to correct problem in exsiting switch gear that utilizes 5/16" all thread to hold C channel barrier for buss spacing, from heating... temp. showing 54.6 C on all threads, buss running at ambient room temp.

Am considering covering all tread with tublar barrier board.


Thanks for any help
 
Replies continue below

Recommended for you

That will likely not work.
If you can surround all three phases you won't see the heating. Or somewhere break the hanger loops with non-metal sections.

Keith Cress
Flamin Systems, Inc.-
 