Hello,
The European standard EN 50522 is describing with full details how to evaluate the touch voltage.
Item 5.4.2 is depicting a design process which is summarized in a flow chart in Figure 5 in the standard.
In my case:
The criteria of earth potential rise (Ue) < double the allowed touch voltage is not met.
The design flow chart in leading me to take “recognized specified measures M” which are also detailed in the standard – in Annex E of the standard.
Table E.1 of the standard is attached.
My position in the table is the last bottom row (tf<5s & UE> 4 x Utp) and according to the standard I need to “Proof UT < Utp.
The problem I have is that I cannot find in the standard how to calculate UT, which is the actual prospective touch voltage.
Does anyone know where this calculation is described in EN standards (or IEC)?