In the old-time was common to specify stainless steel or aluminum enclosure for NEMA 4X application. Perhaps PVC or non-metallic compound were available or just introduced in the market.

Does PV or Polyvinyl meet today the requirement for NEMA 4X in HV Utility applications?

NEMA_Enclosure_Rating_pivlrw.jpg
 
Replies continue below

Recommended for you

Glass reinforced polyester material was the recommended already 30 years ago. Now it could be the P.V.C.turn. I got once polyvinyl boxes from Australia-I guess-for NEMA 9 [Hazardous Location class II Division I] instead of cast iron.
 
PVC is often problematic in sunlight exposed applications, the UV makes it more susceptible (i.e. less resistant) to impacts, which is a problem for enclosures. Still, people use PVC because it is inexpensive. FRP (Fiber Reinforced Plastic) is the preferred material for non-metallic N4X, but is more expensive.