e104909
Civil/Environmental
- Aug 13, 2011
- 65
Id like to seek your opinion on this case. I am struggling to convince myself with this assumption from a senior engr.
The concrete joists (that connects to the girder) in ETABS were released in M22, M33, and T. The actual connection detail of the joist to beam is a standard hook which is fully develop in tension. The ETABS model assumes the slab to be a membrane element.
With the Pin end condition, the number of rebars at negative moment is 3-#8. If I make this fixed (w/o releases), then of course the number of bars in the negative moment are short. The argument is that the moment will be redistributed to the positive region and if the positive moment is capable of handling the redistributed moment then it should be fine. This assumption is only at the end spans of a continuous joists and only at the end where it connects to primary beam which makes the joist to be a secondary beam.
Is this assumption valid?
Will the concrete have to crack first in the negative region before it redistribute it to the positive region?
Since this is concrete, shouldnt we stick to traditional fixed end condition and let the joists be designed for negative moment as well?
Regards,
E104909
Civ-Str P.E.
The concrete joists (that connects to the girder) in ETABS were released in M22, M33, and T. The actual connection detail of the joist to beam is a standard hook which is fully develop in tension. The ETABS model assumes the slab to be a membrane element.
With the Pin end condition, the number of rebars at negative moment is 3-#8. If I make this fixed (w/o releases), then of course the number of bars in the negative moment are short. The argument is that the moment will be redistributed to the positive region and if the positive moment is capable of handling the redistributed moment then it should be fine. This assumption is only at the end spans of a continuous joists and only at the end where it connects to primary beam which makes the joist to be a secondary beam.
Is this assumption valid?
Will the concrete have to crack first in the negative region before it redistribute it to the positive region?
Since this is concrete, shouldnt we stick to traditional fixed end condition and let the joists be designed for negative moment as well?
Regards,
E104909
Civ-Str P.E.