cfordyce
Electrical
- Jun 26, 2002
- 55
Hello, I need an approx calculation of energy savings for a fan application. Currently the 44hp motor is run at line voltage and a damper is adjusted to get approx half the rated air flow from the fan (1/2 load). We want to install an frequency inverter to adjust the fan speed to deliver the needed cfm - eliminating the need to adjust the damper.
would moving 1/2 the cfm amount to approx 1/2 the load current to the motor? I know that the motor magnatizing current will remain constant at all loads and that amounts to approx 30% of rated current for a standard AC 3-ph ind mtr.
Mag I = 44A x .3 = 13.2A
therefore load current = 44-13.2 = 30.8A
So really, I'm asking - what does a standard fan curve relating cfm to load (hp) looks like? linear?
Thanks
CAF
would moving 1/2 the cfm amount to approx 1/2 the load current to the motor? I know that the motor magnatizing current will remain constant at all loads and that amounts to approx 30% of rated current for a standard AC 3-ph ind mtr.
Mag I = 44A x .3 = 13.2A
therefore load current = 44-13.2 = 30.8A
So really, I'm asking - what does a standard fan curve relating cfm to load (hp) looks like? linear?
Thanks
CAF