Cost of the installation might be slightly higher for the 1 phase motors as well. It will have a higher FLC (Full Load Current) and will therefore require larger conductors. 1 1 phase 15HP motor (assuming 240V 1 phase) will have an FLC rating of around 73A, requiring conductors capable of handling at least 90A; whereas a 15HP 230V 3 phase motor will have an FLC rating of around 42A, requiring conductors capable of carrying 53A. That represents a signiicant difference in conductor size and cost (albeit the 3 phase motor needs 1 more conductor). From that standpoint then, also go for as high a 3 phase voltage as you have available at the site. In other words if they have 480V 3 phase, use that because the FLC drops to 21A.
If they only have 208V 3 phase, then the cable cost difference will be negligible, but the efficiency may be worse, because if you can even find a 15HP 1 phase motor (they are not common), they will typically be designed for 230V and ACCEPTABLE to run on 208V, but the efficiency will be less than at 230V..