EPS Geofoam at Existing Foundation Wall Condition

Status
Not open for further replies.

LetsTalkEng

Structural
Mar 27, 2018
2
Hello Everyone,

I've come across an interesting existing exterior foundation wall condition and have begun exploring the use of EPS Geofoam as a solution. At a high level I have having difficulty finding the appropriate design parameters, but wonder if it's because I am not asking the right questions. A brief discussion of my condition/problem below.

Existing Condition:
Exterior 12" concrete foundation wall r/w 15M @ 16"c/c each way each face, Running E-W. Typically 10'-0" tall, fully back filled. Floor framing is steel beams with 2 1/2" topping on 1 1/2" metal deck floor framing on the South side. 15' from the West end the basement slab depresses for a theater room. This condition extends 24' until it meets a return wall from the North. Further east of that is an underground garage where the wall is not back-filled on either side. North of the theater room wall, planters are proposed with 4'-0" of planting medium. A contextual section with assumptions is attached.

Now, if that foundation wall get's back filled full height, the loading will be over double what it is capable of sustaining. What I am proposing is to backfill to approximately 3' from t/o basement slab to cover the exterior weeping tip and drainage. From there I will have a geotechnical consultant specify a berm slope extending North and likely West, to prevent any at rest earth pressures and create slope stability. I'll fill this sloped area in with EPS geofoam to 4' below final grade. The final 4' would then be filled with planting soil. My general understanding is that I then have Ko soil pressures from soil + surcharge from at grade down to 4'. The geofoam then transfers the vertical load down to the soil located 3' above t/o slab, where the same Soil+surcharge theory applies.

Why question is what happens across the depth of the geofoam? It can take the vertical stress, but there will be some component in the lateral direction as well. Based on leafing through a few papers, I can loosely calculate Ko using the Poisson's Ratio of the geofoam using Ko = v/(1-v); v=0.15 for mist EPS I have seen. Then I'd use a similar methodology to develop my lateral pressures across this depth as well. I've reached out to EPS suppliers, and although they agree Geofoam is a great option, nobody has committed to providing any kind of design criteria. In addition, the project is not in a seismic region, so the use of Geofoam is foreign territory to the geotchnical consultants as well who have only surmised that I should use the supplier's recommendations, thus taking me full circle.

Looking for any insights or considerations I might be overlooking from suppliers/engineers whom are likely more well versed in the use of Geofoam. Thanks in advance!

Cheers,
LetsTalkEng

 
 https://files.engineering.com/getfile.aspx?folder=b81684ac-9f86-44ff-b341-01f3b8edfb44&file=GEOFOAM_WALL_SECTION.pdf
Replies continue below

Recommended for you

I faced a similar challenge when preparing preliminary concepts for a project a couple years ago. Sadly, I didn't learn much before the project was canceled so I can't share a lot of knowledge with you. I can share two things, though:

Geofoam floats! You probably already considered this, but if you have a seasonal water table that approaches the bottom of your foam, make sure you have sufficient soil back fill on top to hold it down.

Do you know anyone in roadway design? A lot of the EPS/geofoam usage I cam across was for road grading in areas with soils sensitive to settlement from surcharge and bridge abutments. Might be a place to look for more information.
 
I've worked on several roadway transportation projects where we would backfill behind tall retaining walls using Geofoam. I wouldn't call myself an expert and I never take on these projects by myself as Geofoam crosses over a bit of the realm between Structural and Geotechnical, leaning more to the latter. Therefore, we always proceed with our designs under guidance with a hired Geotechnical Engineer. I worked on a recent project where we had a weird hybrid wall where we had a 35ft tall soil nail wall with geofoam blocks behind it. We had a 4ft tall soil backfill above the geofoam (just like you) and part of it had to resist HL-93 truck loading.

With all the being said, I calculate the vertical pressure on the Geofoam to be 3.33 psi. Some of the Geofoams that I work with have an allowable compressive resistance (at 1% deformation) of ~3 to 20 psi. So first be sure that you are below that "yield" strength of the foam. You don't want long term creep issues with the foam. These allowable compressive resistances are substantially low enough to ensure linear behavior of the material that will not have long term creep issues.

Your approach of using the poisson's ratio for calculating the earth pressure is reasonable. Your uniform pressure diagram throughout the height of the Geofoam would be correct. When I look at the picture, it all seems reasonable and I agree with your pressure diagram.

I have one suggestion. Wrap the soil backfill at the planters with a geotextile to keep the backfill separate from the Geofoam.
 