grey25
Civil/Environmental
- Jul 26, 2008
- 2
Hello, I'm not a mechanical engineer so forgive the low level of this question. I'm reading through the proposed changes in the new LEED 2009 (NC) Rating System. For EQ Credit 1 (Outdoor Air Delivery Monitoring), the requirements have changed. Actually a part was added.
Here is the old text:
"Install permanent monitoring systems that provide feedback on ventilation system performance to ensure that ventilation systems maintain design minimum ventilation requirements. Configure all monitoring equipment to generate an alarm when the conditions vary by 10% or more from setpoint, via either a building automation system alarm to the building operator or via a visual or audible alert to the building occupants."
Now, they added this:
"All densely occupied spaces must include CO2 sensors. If the AHU predominantly serves densely occupied spaces, outdoor airflow measurement at the AHU is not required. If the AHU predominantly serves non-densely occupied spaces, outdoor airflow measurement at the AHU is required, in addition to CO2 sensors in the densely occupied spaces."
I'm confused by the newly added material. I would think that one should monitor the airflow at densely occupied spaces because there is more CO2 being expelled by more people breathing and it more critical to measure airflow with the larger number of people.
However, they have it the other way around. They say to measure the less densely occupied areas.
What basic logic am I missing?
Best,
Patricia
I've uploaded the pdf containing the new redlined 2009 NC version if you want to look at the whole thing. The piece I'm asking about is on page 69.
Thanks in advance
Here is the old text:
"Install permanent monitoring systems that provide feedback on ventilation system performance to ensure that ventilation systems maintain design minimum ventilation requirements. Configure all monitoring equipment to generate an alarm when the conditions vary by 10% or more from setpoint, via either a building automation system alarm to the building operator or via a visual or audible alert to the building occupants."
Now, they added this:
"All densely occupied spaces must include CO2 sensors. If the AHU predominantly serves densely occupied spaces, outdoor airflow measurement at the AHU is not required. If the AHU predominantly serves non-densely occupied spaces, outdoor airflow measurement at the AHU is required, in addition to CO2 sensors in the densely occupied spaces."
I'm confused by the newly added material. I would think that one should monitor the airflow at densely occupied spaces because there is more CO2 being expelled by more people breathing and it more critical to measure airflow with the larger number of people.
However, they have it the other way around. They say to measure the less densely occupied areas.
What basic logic am I missing?
Best,
Patricia
I've uploaded the pdf containing the new redlined 2009 NC version if you want to look at the whole thing. The piece I'm asking about is on page 69.
Thanks in advance