ath123
Electrical
- Jan 27, 2005
- 7
I just added a new 120/208 volt standby generator to an existing system. To accommodate the addition, I added a new service entrance breaker which feeds the ATS which feeds the old service entrance equipment. The contractor was to install a new grounding electrode system connected at the new service entrance breaker, pull an equipment grounding conductor to the old service entrance equipment, remove the bonding jumper between the neutral and gound lugs at the old service entrance equipment, and disconnect the old grounding electrode conductor from the old service entrance equipment.
When the contractor went to pull the equipment grounding conductor from the ATS to the old service entrance equipment, he found the conduit had shifted and he was unable to pull in the equipment grounding conductor.
The inspector told him it was OK, but keep the old grounding electrode conductor connection at the old service entrance equipment.
Is this a code violation?
When the contractor went to pull the equipment grounding conductor from the ATS to the old service entrance equipment, he found the conduit had shifted and he was unable to pull in the equipment grounding conductor.
The inspector told him it was OK, but keep the old grounding electrode conductor connection at the old service entrance equipment.
Is this a code violation?