Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Equipment In Front of Arc Rated Switchgear

Status
Not open for further replies.

ThePunisher

Electrical
Nov 7, 2009
384
Hi all, I have a technical query that would require some of your experienced thoughts.

WE have an arc rated MV and LV switchgear provided with arc flash ducting that diverts the arc energy outside the building walls. It was customary in previous designs that we do not place any equipment (panelboards, battery chargers, IT cabinets, etc.)in front of these arc rated switchgear.

However, it occurs to me, that the switchgear is already having mechanical arc mitigation by itself and we should be able to locate certain electrical equipment in front of it. Of course, personnel must still wear the appropriate PPE labeled on the switchgear.

Can we locate small electrical equipment on front of arc rated switchgear and comply only with working clearance requirements? I would think, our reliability folks would argue with me...however, arc flash protection is for personnel safety and not for equipment. Since, the switchgear is already arc rated with proper mechanical strength and energy venting, I would think it will not be an issue placing an equipment on front of it.

regards,
 
Replies continue below

Recommended for you

You may get strenuous objection from site personnel if the proposed equipment is to be located in a potential (or perceived) escape route regardless of the PPE requirement.
 
The entire purpose of buying Arc Resistant gear is to facilitate exactly what you are wanting to do. That's why you paid the big bucks for it. Otherwise you could have just restricted access to qualified workers with the proper PPE.

If your gear is truly certified as Arc Resistant per ANSI C37.20, you should be in the "No PPE required" category to just be in front of it, as long as all the doors are closed, there are no known defects, it has been properly installed and maintained per the mfrs instructions.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor