Equivalent Duct Diameter (Circ-NonCirc) and Pressure Drop

Status
Not open for further replies.

749KDV

Mechanical
Feb 7, 2002
38
The ASHRAE Fundamentals Handbook describes the conversion of equivalent duct sizes from circular to noncircular assuming that you start with a design of a circular duct and then convert. I am starting with an existing rectangular duct arrangement and am trying to add a section of rectangular duct and need to calculate the pressure drop due to friction? I realize that in order to use the Darcy equation, I need to convert to an equivalent circular duct size. Here's my dilemma. What velocity do I use? Is it the velocity through the existing rectangular duct, or through its equivalent circular diameter?
 
Replies continue below

Recommended for you

If you are going to use the Darcy equation, it is the velocity in the circular duct.

But why not take the easy way?

Use table 2 "Equivalent Rectangular Duct Dimensions" in reverse to get the equivalent circular duct.

Enter Figure 9 Friction chart for round duct on the cfm axis and go up to the interstection of the equivalent circular duct size. Read the friction loss per 100 feet on the Y axis.
 
Thanks MintJulep for that quick response. I guess to answer your question as to why I don't utilize the tables, it is because I've developed an Excel spreadsheet that will calculate the pressure drop/100ft. I just wasn't sure which velocity should be used, but now I am.

Thanks again.
 
I think I didn't get it right. If you are using an equivalent circular duct for calculation, velocity should remain same.

 

Graphs to convert the dimensions of rectangular cross-sections into equivalent round duct diameters, are presented in two ways:

a. with constant velocity (same mean hydraulic radius)
b. with constant capacity (equal friction per unit length)

Have a look at the Fan Engineering handbook published by the Buffalo Forge Company.
 
From SMACNA:

De = 1.30((ab)^0.625 / (a + b) ^ 0.25)

where:
a = length of one side of rectangular duct, inches
b = length of adjacent side of rectangular duct, inches
De = circular equivalent of rectangular duct for friction & capacity , inches.

For pressure drop in inches wg / 100 ft of duct I have been using:
PD = (CFM)^1.90 (0.0109132) / (De)^5.02
 