I have 2 transformers on which I could measure THDv on the LV side. 1% on 1st transformer (2.5MVA), 2.1% on the second one (2MVA).
Both Transformers are supplied by the same 13.2kV switchgear
Is there an easy way to calculate the equivalent THDv on the 13.2kV side?

Thanks
 
Replies continue below

Recommended for you

No.

I assume that those two transformers have nothing more in common than the primary voltage. And that they are loaded. The load is what determines THDV to a great extent, probably around half of the THDV contribution is from the load. The only thing you can say for sure is that the 13.2 kV THDV is less than 1%

Aren't there any PT:s on the 13.2 kV side? It is an easy matter to measure there. My guess is that you wil see around .5%

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
Thanks

Yes, transformers are loaded (40% for 1st one, 50% for 2nd one) and supply different gears, so as you said, nothing in commom except primary voltage. Unfortunately, no meters on the 13.2kV side....

My guess is less than 1%, but I was wondering if any calculation method (even approximation) exists.
 
You may review what are loads?

Are there predominantly non-linear loads (such as UPS, VSD, thyristor controlled heaters, Fluorescent lamps etc.)in the transformer which has 2.1% THD?

As such 2.1% at 415V is not a THD level which is a cause for any concern as the tolerable level is much higher.
 
Could part of the harmonic distortion be originating on the supply grid?

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Sorry, I was away a few days.
Loads are mainly motors driven by VSD.
I'm not really concerned by the value itself, as it remains under 3%.
My concern was to try to calculate the value on the 13.2kV side. But it seems clear we can't.
Thanks
 
As far as the %ge harmonic current distortion is concerned, it is same at 415V and 13.2kV side.
 