Thank you Scotty and Pierrepaul for the reply. I don't fully agree with your statements of Large Drop as a solution for my problem. Why ?
You have to know that we engineered the building in 1998. It was a 12m high building. First, we wanted to make a compartmentation around the freezer (+/- 5000m²). We used a lot of ESFR for the rest of the site (12m high, storage 10,3m, racks).
A dry system was not a solution for us (f.e. dry Large Drop),not because the max. storage height is less, but for the next reason.
I know a lot of frozen food-manufacturers are using this (in combination with in-rack-sprinkling) for the moment.
I think the negative results of sprinkling water in a building of -22°C are underestimated: the floor will come up, sprinkling piping is gone and you have to unfreeze the building. The most risk for this case is an accidental damage of a bulb.
Then, we heard about antifreeze-solutions for ESFR. The few tests and experiences were a (false) argument to go for this solution. In a surpression scenario we had a good chance to surpress a beginning rack-fire with max 4 sprinklers and 45000 l of water-glycol-solution.
At this moment I know this was not a good choice. As a matter of fact it's difficult to find other solutions.