ESFR Systems with Conveyors - NFPA 13-2022 14.2.11.4 (4)

Status
Not open for further replies.

skdesigner

Mechanical
Aug 17, 2010
432
0
0
CA
The above reference states that additional sprinklers are not required below belt conveyors up to 4ft wide, where the area below is void of storage.

In my situation I have two conveyors, each approximately 2'-9" in width running parallel with each other, with a 2'-9" gap between them.

Would I be correct in stating that because neither conveyor exceeds 4'-0 in width, no sprinklers are required beneath? Or would I have to look at their widths in aggregate because they are fairly close together (thus treating them like conduits or other 'tightly grouped' obstructions per in 14.2.11.3.4)?

Thanks in advance.
 
Replies continue below

Recommended for you

IMO, I would not put sprinklers below based on your criteria.

Travis Mack, SET, RME-G,
MEPCad, Inc
AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT

 
I know. It is getting a lot different. I had a large project recently and we had a bunch of conveyors. Luckily I was going through the 2022 edition and found that section. The AHJ allowed us to use the 2022, even though 2019 was in force at the time. It had quite a cost savings associated.