SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
I have a typical 500'x250' bent metal purlins on rigid metal frames spaced 25'-0" building.
Eave height is 24', roof pitch is 1 in 12 putting the peak at 34'-5" from underside of metal roof panel to concrete finished floor.
We are protecting wooden pallets stacked to 25'-0" high while maintaining a 3'-0" clearance between the sprinkler and top of storage (wooden pallets).
Looking at ESFR 16.8 sprinklers discharging at 52 psi per Table 12.1.9.1.2(c) "ESFR Protection of Indoor Storage of Idle Wood Pallets"
Minimum spacing is 8', maximum is 10'.
Normally I hang from the top lip of the bent metal purlin running the usual 2 1/2" branch line up in the purlin space.
On this building the first purlin is 0'-7 1/2" measured off the peak to the purlin lip I would hang to and then 5'-0" OC.
If I hang off on of the top purlins the next purlin on the opposite side down is either 6'-3" (to close) or 11'-3" (to far.
The only thing I can do is hang off the purlins on one side until I get to the peak then use trapeze hangers (uni-strut with U hangers) to maintain the 10'-0" spacing down the other side with the actual pipe being 1'-3" from the purlin.
Sprinklers will be 8'-4" OC so I will have 83.33 sq ft head spacing.
Is there any reason, once I travel far enough down the slope to a point where the roof < 30' AFF, where I can have one line spaced at 11'-3 (94 sq. ft. spacing) to once again catch a purlin?
Better to have four or five lines on trapezes than twelve.
Eave height is 24', roof pitch is 1 in 12 putting the peak at 34'-5" from underside of metal roof panel to concrete finished floor.
We are protecting wooden pallets stacked to 25'-0" high while maintaining a 3'-0" clearance between the sprinkler and top of storage (wooden pallets).
Looking at ESFR 16.8 sprinklers discharging at 52 psi per Table 12.1.9.1.2(c) "ESFR Protection of Indoor Storage of Idle Wood Pallets"
Minimum spacing is 8', maximum is 10'.
Normally I hang from the top lip of the bent metal purlin running the usual 2 1/2" branch line up in the purlin space.
On this building the first purlin is 0'-7 1/2" measured off the peak to the purlin lip I would hang to and then 5'-0" OC.
If I hang off on of the top purlins the next purlin on the opposite side down is either 6'-3" (to close) or 11'-3" (to far.
The only thing I can do is hang off the purlins on one side until I get to the peak then use trapeze hangers (uni-strut with U hangers) to maintain the 10'-0" spacing down the other side with the actual pipe being 1'-3" from the purlin.
Sprinklers will be 8'-4" OC so I will have 83.33 sq ft head spacing.
Is there any reason, once I travel far enough down the slope to a point where the roof < 30' AFF, where I can have one line spaced at 11'-3 (94 sq. ft. spacing) to once again catch a purlin?
Better to have four or five lines on trapezes than twelve.