Are there any rules of thumb that would allow a consulting engineer to estimate the water volume in a preaction sprinkler system before the actual system layout is designed by the sprinkler contractor. I need an estimate to define the HP of the air compressor for the system

Thanks

Chaz12
 
Replies continue below

Recommended for you

There isn't much to go on it all depends on the size of the system, the water supply and hazard which has all to do with size of pipe.

On a double interlocked system you are supposed to maintain 50 psi for water pressure to 175 psi.

I looked at a system I did; .30/2000 with a water supply of 70, 50 and 1200 and came up with 719 gallons over40,000 sq. ft. for 0.018 gallons per sq. ft..

A 10,000 sq. ft. system would have around 180 gallons based on the last system I did.

For you, me not knowing particulars, this information is all but useless but maybe it will give some sort of an idea.

Sorry I couldn't be more specific.
 
Thank you, sir. Your post was helpful. Our system is single interlock and I have read that 20 psi in the system is normal. Our hazard is O2 and our pressure may be a little better: 82 static, 68 residual, at 1150 gallons.

But the compressors I looked at on the Viking site show that any volume over 300 gallons gets into a horsepower larger than 1/2. So I am going to tell the electrical engineer to provide a voltage higher than 120.

Thanks again.