I'm working on a rectifier for a drive system that will be supplied by a 625KVA diesel genset. The existing rectifier being used has the usual 3% impedance line reactor as normally specified when a drive is supplied by the mains and this strikes me as both counterproductive (more voltage drop) and superfluous, as even a 625KVA synchronous generator will exhibit a much higher source impedance than the mains. I know that to determine the interrupt capability of the breakers required in the event of a short one uses the subtransient reactance, X"d, to determine the initial current spike (lasting ~ a half to one full cycle), but for the purposes of reducing harmonic distortion and improving rectifier power factor, which reactance value is appropriate? Using the synchronous reactance, Xd, gives what seems like an absurdly high value of inductive reactance (e.g. - 1.2mH). Using the armature time constant, and knowing the resistance of the stator windings, gives an eminently plausible value of 70.3uH. Finally, using X"d gives a somewhat lower than expected, though still plausible, inductance of 38.5uH.
For reference, the following specifications for this 480VAC generator are known:
KVA base rating for reactance values = 825
Xd = 2.80 PU
X'd = 0.13 PU
X"d = 0.09 PU
Ta = 0.019 seconds (armature time constant)
Stator winding resistance = 3.7 milliohms
For reference, the following specifications for this 480VAC generator are known:
KVA base rating for reactance values = 825
Xd = 2.80 PU
X'd = 0.13 PU
X"d = 0.09 PU
Ta = 0.019 seconds (armature time constant)
Stator winding resistance = 3.7 milliohms