antigfk
Electrical
- Mar 26, 2009
- 33
I will have 12 480V generators in parallel with KW and KVAR load sharing connected to a 4160V bus through a bunch of 2500kVA transformers. I am attempting to run a Dynamic motor start study with one 5000HP motor running and one 5000HP motor starting on the 4160V bus. The 5000HP motors are started on a 250% to 350% current ramp soft starter.
Here is my issue:
Upon hitting the start button, the voltage will initially drop. In reality, then generators' AVR's will excite the generator into providing more VAR than the motor requires to start, which will pick the voltage back up to 480V (on the generator terminals) even while the motor is accelerating. I don't know how to simulate this using ETAP.
All the generators are identical - there is no "swing" generator or a "voltage control" generator. They all provide the KW and KVAR required by the load, plus KVAR to raise the voltage to near nominal volts. In ETAP, when I put the generators on "swing", they do not react to correct voltage. When I select "voltage control", the KW output does not change with the load requirements.
I know that there must be one "swing" generator on the system for ETAP to operate correctly. Is there any way I can get the generators to have both properties - swing and voltage control at the same time?
Here's a graph of the voltage vs time during the motor acceleration. The green line is ETAP's calculation (I would expect the curve to look like this if the power source was utility power with no voltage regulation). The red (which I drew in using mspaint) is what I would expect the actual voltage to look like in my scenario.
What do you guys think?
Here is my issue:
Upon hitting the start button, the voltage will initially drop. In reality, then generators' AVR's will excite the generator into providing more VAR than the motor requires to start, which will pick the voltage back up to 480V (on the generator terminals) even while the motor is accelerating. I don't know how to simulate this using ETAP.
All the generators are identical - there is no "swing" generator or a "voltage control" generator. They all provide the KW and KVAR required by the load, plus KVAR to raise the voltage to near nominal volts. In ETAP, when I put the generators on "swing", they do not react to correct voltage. When I select "voltage control", the KW output does not change with the load requirements.
I know that there must be one "swing" generator on the system for ETAP to operate correctly. Is there any way I can get the generators to have both properties - swing and voltage control at the same time?
Here's a graph of the voltage vs time during the motor acceleration. The green line is ETAP's calculation (I would expect the curve to look like this if the power source was utility power with no voltage regulation). The red (which I drew in using mspaint) is what I would expect the actual voltage to look like in my scenario.
What do you guys think?