ETAP Governor Simulation 1

Status
Not open for further replies.

sky2020

Electrical
May 21, 2019
39
Hello,
I have two machines which is 20MW each but the real power output of each generator is 16MW. I modeled the system in ETAP. During transient simulation, the generator Pm output reaches 19MW but actually the power output is 16MW maximum. How to limit the generator output to 16MW? Is there a parameter or anything to tweak?
 
Replies continue below

Recommended for you

Why/how is it physically limited to 16MW? During transients power out of rotating machines can easily exceed the mechanical power in for brief periods; if you're thinking that a 16MW prime mover creates a hard limit you'll find that to not be the case.

I’ll see your silver lining and raise you two black clouds. - Protection Operations
 
Are you sure that the machines are not 20 MVA and 16 MW?
That would be a typical rating.
You can limit the steady state power by limiting the fuel or steam feed to the prime mover.
The added power during transients is often produced by the inertia of the spinning mass of the generator and of the prime mover.
I am in agreement with David's information.
Further, in some sizes of prime power generator a 10% overload is allowed for 1 hour out of 12.



Bill
--------------------
"Why not the best?"
Jimmy Carter
 