Amex12
Electrical
- Sep 29, 2020
- 18
I am trying to model a Wye(ungrounded)/Wye(grounded)/buried delta tertiary transformer in ETAP. The HV side is the source of fault current and is ungrounded as specified. When I model it as a two winding transformer, I am able to select a checkbox for buried tertiary. However, when I place a L-G fault on the Wye(grounded) LV side, I see no ground fault current.
However, when I model this as a three winding transformer with the buried delta as the third winding, when I place a L-G fault on the Wye(grounded) LV side, I see ground fault current.
What is the correct approach here?
However, when I model this as a three winding transformer with the buried delta as the third winding, when I place a L-G fault on the Wye(grounded) LV side, I see ground fault current.
What is the correct approach here?