ETHYLENE STORGE TANKS INSPECTION

Status
Not open for further replies.

MAG1985

Mechanical
Nov 27, 2012
6
HI ALL.
Two liquid ethylene storge tanks are to be inspected almost for the first time since begining of 80s. these tanks are constructed according to:
- CODE OF CONSTRUCTION: API 620 APP. Q, 6TH ED, REV. 2, 1978.
- OTHER SEPCS: SP-4615-41-2, 20-1...for insulation, piping...
the tanks are double wall of:
Inner tank MOC:shell: A-553, bottom/annular: A-553TP. 1/A353
Outer tank MOC:shell: A-283C, bottom/annular: A-283-C/A-283-C
Suspended deck :ALUM-5083-O.

what would be better inspction techniques, methodology, tools.

thanks
 
Replies continue below

Recommended for you

Hire a reputable inspection firm that has a 'stable' of API-653 certified Inspectors, with RBI - Risk Based Inspection experience.. If you can have the design drawings ready, or send them out with your Request for Quote, you should get all your answers for 'free', after they look over your tank and give you a quote/estimate.

Plan on having to get an Internal Inspx on at least one of your tanks; if they are actually identical [or nearly so] and have been in the same service, it may be possible to use Risk-Based-Inspx methods to avoid emptying and cleaning both tanks.
 
Thank you Duwe6.
In fact, these tanks are identical, and of my knowledge, no inspection was done over the 25 years internally. Now it becomes the concern of all technicals and management to prepare inspection considering RBI.
 
I was involved on the periphery of an inspection/repair of an ethane storage tank that operated at a few psig, sounds similar to what you have here. We used CBI to develop the shutdown, warmup and purging procedures as well as the purging, cooldown and recommissioning procedures and they also did the repairs required by the tank (we had external corrosion of the base CS floor resulting in ethane gas leaks from the annular space between the two tanks into the foundation sand support layer.

I was pretty impressed with the people we worked with at CBI, they knew their stuff.
 
"...CBI, they knew their stuff."

I know of no firm that exceeds the institutional knowledge, and abilities of Chicago Bridge & Iron. Period.
 