ngomdiaz
Mechanical
- Jun 8, 2012
- 1
Good Night
I ‘been ask to evaluate the change of diameter of a Pressure Relieve Valve, for a water pump system, We have two Vertical Centrifugal Pumps of various stages, one move by a electrical motor and the other by Diesel Engine, both suctions sea water and discharges to a industrial plant, this water is use for Fire Protection.
The pressure required for the system is 100 psig, the pump have a capacity of 3000gpm.
Someone told me that you need to install a PRV to protect the pipe for overpressure, and that valve have to be localized after the pump discharge and before a check valve, plus the system permit to discharge the exceed of water again to the sea
I first wanted to calculate the Area of the Orifice of the PRV installed so that I can check if the diameter is correct, I know that API 520 tells about calculate the PRV valve but also says discharge capacity is required, and I really don’t know how to calculate that discharge capacity
If I consider the worst scenario than the gate valve localized before the check valve, closes for a failure or a bad operation. And I believe that for a centrifugal pump the PRV don´t need to relieve the hole 3000gpm because this sort of pumps can operate with the discharge close for some time, I think I can estimate a discharge capacity less than 3000 gpm, but I don’t know how. Is there any formula or Code (ASME, API) that permit solve mi problem, maybe in fire pumps systems designs, etc
I really appreciate your help, I Know you guys can help me for taking the right decision… Thanks for your time…
I ‘been ask to evaluate the change of diameter of a Pressure Relieve Valve, for a water pump system, We have two Vertical Centrifugal Pumps of various stages, one move by a electrical motor and the other by Diesel Engine, both suctions sea water and discharges to a industrial plant, this water is use for Fire Protection.
The pressure required for the system is 100 psig, the pump have a capacity of 3000gpm.
Someone told me that you need to install a PRV to protect the pipe for overpressure, and that valve have to be localized after the pump discharge and before a check valve, plus the system permit to discharge the exceed of water again to the sea
I first wanted to calculate the Area of the Orifice of the PRV installed so that I can check if the diameter is correct, I know that API 520 tells about calculate the PRV valve but also says discharge capacity is required, and I really don’t know how to calculate that discharge capacity
If I consider the worst scenario than the gate valve localized before the check valve, closes for a failure or a bad operation. And I believe that for a centrifugal pump the PRV don´t need to relieve the hole 3000gpm because this sort of pumps can operate with the discharge close for some time, I think I can estimate a discharge capacity less than 3000 gpm, but I don’t know how. Is there any formula or Code (ASME, API) that permit solve mi problem, maybe in fire pumps systems designs, etc
I really appreciate your help, I Know you guys can help me for taking the right decision… Thanks for your time…