We have a core loss test that failed the 10C / 18F degrees rise requirement. I’m interested in understanding the significance (beyond just degraded lamination insulation… where is it degraded and how much risk would it pose to rewind without core replace/restack). I occasionally review core loss tests with the help of our shops, but I’m not an expert in figuring out what is causing the patterns and what is the significance and my usual go-to guys for this type of question are unavailable. So that’s why I’m asking opinions here.
Details
[ul]
[li]50 hp 2 pole motor. Manufactured in the 1970’s by Siemens Allis[/li]
[li]Test was conducted with an excitation equivalent of 105% rated backiron flux density calculated as per IEEE Std. 432.[/li]
[li]As-found pre-burnout test (not included) hottest spot after 30 minutes was 24F rise.[/li]
[li]Burnout was conducted at/below 650F.[/li]
[li]Post burnout thermography test (attached):[/li]
[li]...Slides 1- 4 10 minute rises 13/14/14/31 (see 1 below)[/li]
[li]...Slides 5-8 20 min rises 19 / 26 / 18 / 18[/li]
[li]...Slides 9-13 30 minute rises 24 / 30 / 29 / 26[/li]
[li]The post burnout core loss is 3.38 W/Lb.[/li]
[/ul]
My initial thoughts:
[ul]
[li]1. I’m inclined to discount the 31 on page 4. I don’t see similar number on page 8. I’m not sure what feature on page 4 it represents. Is it the white spot around 3… maybe that’s a reflection of something?[/li]
[li]2. Looking at the bore (tooth tips), it looks cooler on one end and hotter on the other end with a distinct stripe. However when they swap viewing ends it always look like you’re looking from the hotter end. Example compare slides 5 and 7… opposite ends based on positioning of the large and small cables, but they both look like the cooler part of the bore is on the far end from the viewer. Is this a viewing angle problem or is the imager averaging the top of the teeth with the empty slots which always looks cooler on the far end?[/li]
[li]3. The hottest spots are show in the slots where some degree of cavity effect is expected. I don’t really see any pattern there, just uniformly hot in the slots is all I can discern.[/li]
[li]There is no obvious surface distress of the bore (teeth ends) or the slots[/li]
[li]The temperature continued to rise between 20 minutes and 30 minutes=[/li]
[li]Looks like just uniform degradation of the bulk lamination insulation as far as I can tell. But doesn't look particularly severe to me. [/li]
[/ul]
The motor I’d say is on the lower/middle end of criticality (not high).
What do you see in the images and what does it tell you about the core condition and risk of rewinding without replacing/restacking the core.
=====================================
(2B)+(2B)' ?
Details
[ul]
[li]50 hp 2 pole motor. Manufactured in the 1970’s by Siemens Allis[/li]
[li]Test was conducted with an excitation equivalent of 105% rated backiron flux density calculated as per IEEE Std. 432.[/li]
[li]As-found pre-burnout test (not included) hottest spot after 30 minutes was 24F rise.[/li]
[li]Burnout was conducted at/below 650F.[/li]
[li]Post burnout thermography test (attached):[/li]
[li]...Slides 1- 4 10 minute rises 13/14/14/31 (see 1 below)[/li]
[li]...Slides 5-8 20 min rises 19 / 26 / 18 / 18[/li]
[li]...Slides 9-13 30 minute rises 24 / 30 / 29 / 26[/li]
[li]The post burnout core loss is 3.38 W/Lb.[/li]
[/ul]
My initial thoughts:
[ul]
[li]1. I’m inclined to discount the 31 on page 4. I don’t see similar number on page 8. I’m not sure what feature on page 4 it represents. Is it the white spot around 3… maybe that’s a reflection of something?[/li]
[li]2. Looking at the bore (tooth tips), it looks cooler on one end and hotter on the other end with a distinct stripe. However when they swap viewing ends it always look like you’re looking from the hotter end. Example compare slides 5 and 7… opposite ends based on positioning of the large and small cables, but they both look like the cooler part of the bore is on the far end from the viewer. Is this a viewing angle problem or is the imager averaging the top of the teeth with the empty slots which always looks cooler on the far end?[/li]
[li]3. The hottest spots are show in the slots where some degree of cavity effect is expected. I don’t really see any pattern there, just uniformly hot in the slots is all I can discern.[/li]
[li]There is no obvious surface distress of the bore (teeth ends) or the slots[/li]
[li]The temperature continued to rise between 20 minutes and 30 minutes=[/li]
[li]Looks like just uniform degradation of the bulk lamination insulation as far as I can tell. But doesn't look particularly severe to me. [/li]
[/ul]
The motor I’d say is on the lower/middle end of criticality (not high).
What do you see in the images and what does it tell you about the core condition and risk of rewinding without replacing/restacking the core.
=====================================
(2B)+(2B)' ?