I've been monitoring Harmonics at a 911 call center. They have two 12.5 KVA, 1-phase UPS at 240 volt. The 208 volt system has a boost transformer for each for the 240 volt.
I've review the IEEE 519-1992 document. 3.5% is the highest THD that I've measure at the line side of the system. So, it appears that the system voltage harmonics are below the 5% standard called out in this document. However, it appears that the current harmonics measured might be outside outside the IEEE standard with THD varying between 8 and 22.
If the voltage harmonics are ok, are the current harmonics a concern?
I've review the IEEE 519-1992 document. 3.5% is the highest THD that I've measure at the line side of the system. So, it appears that the system voltage harmonics are below the 5% standard called out in this document. However, it appears that the current harmonics measured might be outside outside the IEEE standard with THD varying between 8 and 22.
If the voltage harmonics are ok, are the current harmonics a concern?