edienberg
Electrical
- Oct 18, 2006
- 16
Was wondering if anybody had some thoughts on this?
What is a recommended method for evaluating insulation resistance (IR) test results of Heat Trace cables? The system in question was put into service 10 years ago, and to the best of my knowledge IR tests have not been done routinely so there is not any histortic data to compare to.
Below how many M-Ohms would the cable be considered bad and below how many M-Ohms would it be considered to have reduced life?
From IEEE 515-1997:
4.1.2 Insulation resistance test
The resistance of the insulation shall be measured between conductors and the metallic outer covering, or a specially applied conductive metal ground plane, by means of dc voltage of 1000 Vdc for mineral insulated heaters and 2500 Vdc for polymer insulated heaters. The measured value shall not be less than 50 M-Ohms.
Erik
What is a recommended method for evaluating insulation resistance (IR) test results of Heat Trace cables? The system in question was put into service 10 years ago, and to the best of my knowledge IR tests have not been done routinely so there is not any histortic data to compare to.
Below how many M-Ohms would the cable be considered bad and below how many M-Ohms would it be considered to have reduced life?
From IEEE 515-1997:
4.1.2 Insulation resistance test
The resistance of the insulation shall be measured between conductors and the metallic outer covering, or a specially applied conductive metal ground plane, by means of dc voltage of 1000 Vdc for mineral insulated heaters and 2500 Vdc for polymer insulated heaters. The measured value shall not be less than 50 M-Ohms.
Erik