stuckbreaker
Can the accuracy of a metering class CT be treated similarly to a C-rated protection class CT where the rating still holds as long as the voltage produced by the CT does not exceed its rating, or is the rated burden the maximum permissible connected burden?
For example, a C800 CT is rated at 20x nominal current (say 5A) and a burden of 8Ω. If it is connected to a load of 16ohms, the CT would hold its accuracy class at 10x nominal current (10*5A*16Ω = 800).
If I have a 100/5A 0.3B1.2 metering CT with TRF=4.0, the accuracy class should be held from 10% to 100%*TRF, so up to 20A. Does this mean that the connected burden can exceed the nominal burden rating as long as 20A*1.2Ω=24V is not exceeded? Would the metering CT still hold its accuracy at a connected burden of 2.4Ω as long as the current does not exceed 10A?