Hi, I am sizing an exhaust fan for a washroom located 20 meters below ground in a subway station. The horizontal run of the exhaust ducg is 80 meters, plus 8 elbows. The duct ends up at the exterior wall above ground. The exhaust air is 300CFM.
My calculation shows me the pressure drop of the whole duct is 0.5 in.w.c., plus pressure drops caused by fire dampers, control dampers, exterior wall louvers, the total pressure drop is 1.2 in.w.c.
This is the first time I size a small exhaust fan for such a long duct. I don't know will it work.
My question is, can a 1.5 in.w.c. Centrifugal inline fan do the job? Is a second boost fan needed?
Would anybody who has the experience ask my question?