mayoj
Mechanical
- May 21, 2014
- 3
I've been given a project to replace 2 existing exhaust fans. There are 4 total in two systems which are similar but operate separately. Each system has a duty fan and a stand-by. A few years ago the other two fans were replaced with smaller capacity fans. The original fans were 48,000 cfm and the new fans are 36,000 cfm. They are captureing exhaust gases from a system of furnaces which burn natural gas. When I questioned how the new fans were sized I was told they took air flow measurements one day with 10 furnaces running and that's the number they used. I am not covinced this is the worse case scenario. I know I have 10 furnaces which could be running at the same time. Each furnace can put out 3,600,000 BTU/hr. The actual BTU's varies by product being run in them. Natural gas is roughly 1000 BTU/cu.ft and it requires 10 parts air to 1 part natural gas for combustion. When I work this out, it gives me approximately 2,400,000 cfm of combustion products I need to exhaust which makes no sense as my fans could not physically do that.
as you can see, I'm not a ventilation guy and I could use some assistance on this. I basically need to know how to calculate the volume flow for products of combustion from my furnaces.
as you can see, I'm not a ventilation guy and I could use some assistance on this. I basically need to know how to calculate the volume flow for products of combustion from my furnaces.