spieng89
Structural
- Jun 30, 2015
- 172
I have 1-story structure where I am adding a sub-level below the roof. In order to support the increased load at this level, I am cutting existing columns mid span and adding beefier columns below to support the sub-level and new foundations. The existing columns will rest on transfer base plates sitting atop of the new column below. Essentially a column splice. Done this a few times, no issues but never a large amount of columns at one time.
My question is how many of these columns would you allow a contractor to cut/shore at one time. Of course the contractor wants to cut/shore all the columns at one time. None of these columns are a part of the lateral system, gravity columns only. There are about 30 columns in an area.
I can't find structural reason why they couldn't do this, they'd complete the install of new columns before 180 days (which is the time limit I use based on IBC section 3103 to consider a structural condition temporary), nothing in OSHA barring this. Only my gut feeling of not wanting a good portion of the roof being supported on temporary shoring. Another engineer is responsible for the shoring design.
I'm thinking of telling them to shore every other column for no other reason of sleeping well at night. But would like to have a more robust reasoning behind the decision if there is pushback. Any thoughts?
My question is how many of these columns would you allow a contractor to cut/shore at one time. Of course the contractor wants to cut/shore all the columns at one time. None of these columns are a part of the lateral system, gravity columns only. There are about 30 columns in an area.
I can't find structural reason why they couldn't do this, they'd complete the install of new columns before 180 days (which is the time limit I use based on IBC section 3103 to consider a structural condition temporary), nothing in OSHA barring this. Only my gut feeling of not wanting a good portion of the roof being supported on temporary shoring. Another engineer is responsible for the shoring design.
I'm thinking of telling them to shore every other column for no other reason of sleeping well at night. But would like to have a more robust reasoning behind the decision if there is pushback. Any thoughts?