mmodfr2013
Structural
- Feb 22, 2017
- 10
I'm looking at an existing concrete structure, the owner is interested in adding some additional floors. The original structure dates to the late 60's.
-The columns are reinforced with #11 vertical bars and #3 ties, which was OK under ACI 318-63.
-Current ACI code requires #11 vertical bars to have a #4 tie, minimum.
-We are adding enough additinoal vertical load to the columns that some sort of work will be required to strengthen the columns, just based on strength requirements.
-Project constraints limit the amount of width we can add to the column to 4" total in one direction (i.e., we can add 2" to the left and right side), we have more leeway on the top and bottom.
What are my options to reinforce the column to meet the minimum tie requirement, short of adding concrete to all four sides and a #4 tie? I don't really have room to add vertical bars on teh left and right side with the 2" constraint? I suppose FRP is an option, but I don't have the experience to give a cost comparison on that solution.
-The columns are reinforced with #11 vertical bars and #3 ties, which was OK under ACI 318-63.
-Current ACI code requires #11 vertical bars to have a #4 tie, minimum.
-We are adding enough additinoal vertical load to the columns that some sort of work will be required to strengthen the columns, just based on strength requirements.
-Project constraints limit the amount of width we can add to the column to 4" total in one direction (i.e., we can add 2" to the left and right side), we have more leeway on the top and bottom.
What are my options to reinforce the column to meet the minimum tie requirement, short of adding concrete to all four sides and a #4 tie? I don't really have room to add vertical bars on teh left and right side with the 2" constraint? I suppose FRP is an option, but I don't have the experience to give a cost comparison on that solution.