-
1
- #1
deereman
Structural
- Mar 30, 2005
- 44
I've been asked to analyze an existing elevated slab to be used as storage. The slab itself is 6" thick (d=5.75) 3000 psi with #4 @ 6" o.c.spanning 12'-10" from concrete beam to concrete beam. Temp steel in other direction is #3 at 10" o.c. The original design drawings from 1968 say the floor is designed to a live load of 140 psf. Based on moment i get an allowable live load of approx. 120 psf and based on shear it can't withstand its own dead load. Can someone check behind me. I can't believe this slab was undersized by this much. Was shear strength calculated different in 1968? Also, the majority of the beams on one side have exposed reinforcing steel. It looks like some chemical previously used caused spalling of the concrete(these will be replaced.) The beams everywhere else look in good shape and can withstand 140psf. Is a visual inspection of these 'good beams' sufficient or should I require some testing to be done?