Can anybody help me what i missed?
I modeled an existing mat foundation of heat exchanger using plate element of STAAD Pro.
Slab Thickness is 1100mm reinforced with 28mm dia spaced at 200 center-to-center.
The provided steel is only 3.078sq.mm/mm with Moment cap = 1,131 kn-m/m (existing configuration).
When i modeled this foundation, STAAD computed the Maximum moment to be 1,798 kN-m/m with steel requirement of 5.10 sq.mm/mm which would then create problem because the existing structure fail, and this has been in the field for long time with no problem.
Our goal is to investigate the existing structure to accommodate additional load for a new equipment replacement which is 3.5% heavier than the original weight.
Attached is my STAAD model for reference.
Thank you.