SprinklerDesigner2
Mechanical
- Nov 30, 2006
- 1,251
Four story high end motel/resort built on the coastal flatlands.
Here is a cross section from the original plans dated 1970's:
The existing fire protection is four standpipes supplied from a 1,500 gpm 90 psi fire pump that also supplies one sprinkler head per floor in the 100 sq ft storage room adjacent to the standpipe. This single sprinkler head is controlled by a 2 1/2" O.S.&Y. floor control valve with tamper switch.
It's obvious to me the original design featured a full fire sprinkler system throughout but somewhere along the lines someone figured out the fire sprinkler was not required so it never went in. I don't think the entire building has more than 12 heads and that includes the ones in the trash chute.
On the drawing it appears there might be a floor above the fourth but it's really a high ceiling skylight.
Fourth floor slab is 25' above first floor slab. While there I checked the height with my laser just to make sure and it is what it is.
The existing fire pump is in deplorable condition to the point where it need to be replaced (you would have to see it to believe it) but why the expense? I did the calcs and a manual wet standpipe works great even with 100 psi at the tops of the standpipes.
Then the other question would be why the standpipe at all? We would leave the standpipe to feed only the sprinklers.... a bit of an overkill with 2 1/2" pipe feeding a single 1/2" sprinkler.
As far as calculating the standpipe to a manual wet that should be my deal but the decision regarding deleting the standpipe altogether would probably be the call of the architect of record who is no longer with us. How would you approach this?
Here is a cross section from the original plans dated 1970's:
The existing fire protection is four standpipes supplied from a 1,500 gpm 90 psi fire pump that also supplies one sprinkler head per floor in the 100 sq ft storage room adjacent to the standpipe. This single sprinkler head is controlled by a 2 1/2" O.S.&Y. floor control valve with tamper switch.
It's obvious to me the original design featured a full fire sprinkler system throughout but somewhere along the lines someone figured out the fire sprinkler was not required so it never went in. I don't think the entire building has more than 12 heads and that includes the ones in the trash chute.
On the drawing it appears there might be a floor above the fourth but it's really a high ceiling skylight.
Fourth floor slab is 25' above first floor slab. While there I checked the height with my laser just to make sure and it is what it is.
The existing fire pump is in deplorable condition to the point where it need to be replaced (you would have to see it to believe it) but why the expense? I did the calcs and a manual wet standpipe works great even with 100 psi at the tops of the standpipes.
Then the other question would be why the standpipe at all? We would leave the standpipe to feed only the sprinklers.... a bit of an overkill with 2 1/2" pipe feeding a single 1/2" sprinkler.
As far as calculating the standpipe to a manual wet that should be my deal but the decision regarding deleting the standpipe altogether would probably be the call of the architect of record who is no longer with us. How would you approach this?