I have a situating where mechanical engineers want to add an AC unit on existing roof. The roof construction is typical steel bar joist, metal deck, light weight concrete and water resisting membrane. Of course there is a suspended ceiling system. Nothing facny.
The building was designed in the late sixties. It appears that the structure was designed by an architect. The joists are spaced 6 foot on center with metal deck of unspecified height and three inches of concrete of unspecified density or type. This is of the plans sections and details.
It appears that the concrete is insulative type (I assume a weight of 2 PSF per inch of thickness). The deck, I assume is one inch high based on 6 foot span. The steel joists are 16H7. Using 20PSF live load and computing 14-PSF dead load I am able to determine that the joist load carrying capacity is almost maxed for its span. This is based on SJI’s load tables for 16H7.
I am able to locate the AC unit so that two sides will be bearing directly on steel beams that are well below their allowable stress and deflection. No problem.
I followed procedure that was published by Vulcarft in the 80 about designing joists for concentrated loads. Here is what I found:
1. The total moment capacity of 16H7 is above the new imposed uniform and concentrated load. From simple strength of material (shear and moment diagram)
2. The end reaction capacity of the joist seat is slightly above the actual reactions from the imposed uniform and concentrated loads.
3. When determining the uniform load on the joist using Vulcraft’s procedure, I came up with a “computed equivalent uniform load” that is about 10 pounds per foot larger that the joist allowable uniform load capacity.
I know that all the loads that I computed are based on full LL and DL combination acting simultaneously. How does everyone feel about the excess 10 pounds per foot?
I plan on calling Vulcraft and chatting with their engineers. Meanwhile, if you were in my shoes, what would you do?
The building was designed in the late sixties. It appears that the structure was designed by an architect. The joists are spaced 6 foot on center with metal deck of unspecified height and three inches of concrete of unspecified density or type. This is of the plans sections and details.
It appears that the concrete is insulative type (I assume a weight of 2 PSF per inch of thickness). The deck, I assume is one inch high based on 6 foot span. The steel joists are 16H7. Using 20PSF live load and computing 14-PSF dead load I am able to determine that the joist load carrying capacity is almost maxed for its span. This is based on SJI’s load tables for 16H7.
I am able to locate the AC unit so that two sides will be bearing directly on steel beams that are well below their allowable stress and deflection. No problem.
I followed procedure that was published by Vulcarft in the 80 about designing joists for concentrated loads. Here is what I found:
1. The total moment capacity of 16H7 is above the new imposed uniform and concentrated load. From simple strength of material (shear and moment diagram)
2. The end reaction capacity of the joist seat is slightly above the actual reactions from the imposed uniform and concentrated loads.
3. When determining the uniform load on the joist using Vulcraft’s procedure, I came up with a “computed equivalent uniform load” that is about 10 pounds per foot larger that the joist allowable uniform load capacity.
I know that all the loads that I computed are based on full LL and DL combination acting simultaneously. How does everyone feel about the excess 10 pounds per foot?
I plan on calling Vulcraft and chatting with their engineers. Meanwhile, if you were in my shoes, what would you do?