Logan82
Structural
- May 5, 2021
- 212
Hi,
I have a situation where a Charpy test indicates less than 20 Joules at 0°C for the main beams of an old existing steel structure on which there is a hoist used to lift a single load of 30 metric tons. The crane members are not covered by an envelope, so therefore the structure can sometimes be at a temperature of -30°C. There are 2 main beams, with no redundancy.
Here are the things I worry about from what I understand of the situation when the temperature of the structure is below 0°C:
- Fatigue. However I believe I can calculate the number of fatigue cycles remaining using the Charpy value.
- Ductility of the structure, since it does not respect the minimums presented in the Handbook of steel Construction 10th Edition:
One solution is to limit the use of this building when the temperature is at 0°C or higher. However this is not feasible in reality.
In CSA S16-19, it says "Statically loaded structures that are subjected to low temperature do not normally require the use of notch-tough steel. In these structures, brittle fracture can normally be avoided by following the design and fabrication criteria provided in this Standard and CSA W59."
Source: CSA S16-19 31.1.1
Also:
"Dynamic loading shall be taken as a loading condition that creates strain rates greater than 10–3 s–1 but less than 1 s–1. Impact loading shall be taken as a loading condition that creates strain rates greater than 0.1 s–1. The impact of stress concentration shall be included in the evaluation of the strain rate."
Source: CSA S16-19 31.3.2
My questions are:
• How can I calculate the strain rate in my structure to know if the live load is an impact load or a dynamic load? In my case, I have a live load, seismic load, and wind load, however the live load is the most important load.
• Is there an other solution to this problem other than verifying if this structure can be classified as statically loaded?
I have a situation where a Charpy test indicates less than 20 Joules at 0°C for the main beams of an old existing steel structure on which there is a hoist used to lift a single load of 30 metric tons. The crane members are not covered by an envelope, so therefore the structure can sometimes be at a temperature of -30°C. There are 2 main beams, with no redundancy.
Here are the things I worry about from what I understand of the situation when the temperature of the structure is below 0°C:
- Fatigue. However I believe I can calculate the number of fatigue cycles remaining using the Charpy value.
- Ductility of the structure, since it does not respect the minimums presented in the Handbook of steel Construction 10th Edition:

One solution is to limit the use of this building when the temperature is at 0°C or higher. However this is not feasible in reality.
In CSA S16-19, it says "Statically loaded structures that are subjected to low temperature do not normally require the use of notch-tough steel. In these structures, brittle fracture can normally be avoided by following the design and fabrication criteria provided in this Standard and CSA W59."
Source: CSA S16-19 31.1.1
Also:
"Dynamic loading shall be taken as a loading condition that creates strain rates greater than 10–3 s–1 but less than 1 s–1. Impact loading shall be taken as a loading condition that creates strain rates greater than 0.1 s–1. The impact of stress concentration shall be included in the evaluation of the strain rate."
Source: CSA S16-19 31.3.2
My questions are:
• How can I calculate the strain rate in my structure to know if the live load is an impact load or a dynamic load? In my case, I have a live load, seismic load, and wind load, however the live load is the most important load.
• Is there an other solution to this problem other than verifying if this structure can be classified as statically loaded?