I have a job where a client wants to add some solar panels to the roof of his house. The existing house is 26’-6” wide and the roof is framed with trusses at 2’-0” o.c with 2x4 chords and web members. The home was built in the 80’s in the Northeast where the ground snow load is currently 30psf and has a 5 pitch.
After inspection/measuring the truss was placed into a computer program and run with the new loading conditions (running both balanced and unbalanced conditions together with attic storage loading). I am getting what I would think are some peculiar results. From what I can tell, the truss system is way over designed. My max compressive load is around 2,500# giving me a fc=425psi. The existing members are Hem-Fir #1 with an Fc = 1350psi*1.15*1.15 = 1785psi. Is it common for a truss like this to be overdesigned?
I am used to seeing trusses with members stressed at 99%-101%.... but I can’t really think of anything the mfr could have done to increase the efficiency of the system (not like they could use smaller chords or space the trusses further apart).
After inspection/measuring the truss was placed into a computer program and run with the new loading conditions (running both balanced and unbalanced conditions together with attic storage loading). I am getting what I would think are some peculiar results. From what I can tell, the truss system is way over designed. My max compressive load is around 2,500# giving me a fc=425psi. The existing members are Hem-Fir #1 with an Fc = 1350psi*1.15*1.15 = 1785psi. Is it common for a truss like this to be overdesigned?
I am used to seeing trusses with members stressed at 99%-101%.... but I can’t really think of anything the mfr could have done to increase the efficiency of the system (not like they could use smaller chords or space the trusses further apart).