Expansion Joint Required?

Status
Not open for further replies.

CTSeng

Structural
Jan 21, 2003
125
Single story building masonry walls (~16' tall) with steel deck on bar joists. 260'x80' With one interior support line and joist spanning short direction. It will be temperature controlled i.e. AC. Feels like a border line situation and debating whether to expansion joint or not?
 
Replies continue below

Recommended for you

I usually use about 300 feet for the cutoff, give or take a few feet and depending on irregularities and other such circumstances.
 
The National Concrete Masonry Association has a detailed report (TEK 10-2A)on control joints for concrete masonry walls.

Their phone number is (703) 713-1900 and their
web page is
You can down load there guides for free.
 