Check the attached photo of a gasoline station.


The two panel boxes at the center of the photo (in the corner of the station) are standard panels (IP-67), which enclose standard circuit breakers for the main gas pumps of the station.

They are less than 7 linear meters on separation.

I would like to ask you, if you have experience on electrical EX-proof facilities:

Is there any mistake here? Or is everything right according to the EX-proof codes?
 
Replies continue below

Recommended for you

Under the Canadian Electrical Code the separation must be 4.5 meters. An inspector may require the length of the hose plus 4.5 Meters radius.