ACI 360-10 provides recommendations for unreinforced slabs on grade contraction joint spacing of 24 to 36 times thickness of slab
ACI 360-10 8.3 speaks to 0.5% reinforcement to eliminate the need for contraction joints
ACI 360-10 8.1 notes benefits of reinforcement allow for "use of longer joint spacings than unreinforced slabs"
ACI 332-08 8.6.2 recommended interpolating from 0.1% for 24 x slab thickness to 0.5% for 100 x slab thickness spaced joints.
While this statement appears to have been removed in later versions of ACI 332, it appears to be a rational approach.
Can anyone comment on:
Where this provision came from?
Why it might have been removed?
If your opinion is it is not a rational approach, why?
Are you aware of any other recommendations from ACI for increasing contraction joint spacing based on reinforcement ratio (for <0.5%)?
ACI 360-10 8.3 speaks to 0.5% reinforcement to eliminate the need for contraction joints
ACI 360-10 8.1 notes benefits of reinforcement allow for "use of longer joint spacings than unreinforced slabs"
ACI 332-08 8.6.2 recommended interpolating from 0.1% for 24 x slab thickness to 0.5% for 100 x slab thickness spaced joints.
While this statement appears to have been removed in later versions of ACI 332, it appears to be a rational approach.
Can anyone comment on:
Where this provision came from?
Why it might have been removed?
If your opinion is it is not a rational approach, why?
Are you aware of any other recommendations from ACI for increasing contraction joint spacing based on reinforcement ratio (for <0.5%)?