I'm hoping that I can get some advice from this forum. I recently built a house with two a/c units. Upstairs I have a 3 Ton unit and downstairs I have a 5 Ton unit. Both are Amana GUIC/D units.
Prior to my one year inspection, I had an independent inspection by an heating and air conditioning company. The results of this inspection said that my Total Static Pressure on the 5 ton unit was over 1.0+ and on the 3 ton unit it was .72. The specification sheet for the units says that the maximum External Static Pressure should be .6 and optimal pressure should be .5. The inspector said that the returns on both units were insufficient. There are three 10 inch returns on the 5 ton unit (1 upstairs and 2 downstairs), and one 12 ince return on the 3 ton unit.
I notified the builder who brought the installer out along with an Amana field rep. They reported that their measurements indicated that the pressure was in the .2 to .3 range and that no action was required.
The contracted inspector provided these results for measuring Total Static Pressure:
3-Ton Unit
Total Static Pressure: .72
Static Pressure Return: .3
Static Pressure Supply: .2
Static Pressure Coil: .22
5-Ton Unit
Total Static Pressure: 1.0
Static Pressure Return: .5
Static Pressure Supply: .4
Static Pressure Coil: .20
My suspicion is that the installer measured only at the coil, which provided the results they indicated. Again the spec sheet for the unit lables "External Static Pressure", which the inspector indicated was the same as "Total Static Pressure."
Three questions:
1. Are they the same?
2. Did the inspector calculate the TSP correctly?
3. Any advice on how to approach the installer if there is an error?
Thanks in advance for any help.
Prior to my one year inspection, I had an independent inspection by an heating and air conditioning company. The results of this inspection said that my Total Static Pressure on the 5 ton unit was over 1.0+ and on the 3 ton unit it was .72. The specification sheet for the units says that the maximum External Static Pressure should be .6 and optimal pressure should be .5. The inspector said that the returns on both units were insufficient. There are three 10 inch returns on the 5 ton unit (1 upstairs and 2 downstairs), and one 12 ince return on the 3 ton unit.
I notified the builder who brought the installer out along with an Amana field rep. They reported that their measurements indicated that the pressure was in the .2 to .3 range and that no action was required.
The contracted inspector provided these results for measuring Total Static Pressure:
3-Ton Unit
Total Static Pressure: .72
Static Pressure Return: .3
Static Pressure Supply: .2
Static Pressure Coil: .22
5-Ton Unit
Total Static Pressure: 1.0
Static Pressure Return: .5
Static Pressure Supply: .4
Static Pressure Coil: .20
My suspicion is that the installer measured only at the coil, which provided the results they indicated. Again the spec sheet for the unit lables "External Static Pressure", which the inspector indicated was the same as "Total Static Pressure."
Three questions:
1. Are they the same?
2. Did the inspector calculate the TSP correctly?
3. Any advice on how to approach the installer if there is an error?
Thanks in advance for any help.